Data centres are no longer designed around a single, predictable load. AI hardware is pushing rack densities well beyond what many cooling strategies were intended for. For energy modelling teams, the question is no longer whether a data hall can be cooled, but how that cooling will behave as IT loads change through the year.
Answering that question requires a detailed model, where all inputs are collectively evaluated for each timestep. The new liquid cooling and server rack functionality in IESVE 2026, available as a premium feature within ApacheHVAC, is designed to easily model racks, thermal zones, airflow controls and liquid / hybrid cooling loops.

Figure 1: Strengths of Modelling Data Centres in IESVE
Data centres have significant energy demands, and cooling efficiency has a direct effect on operating cost and carbon performance. Dynamic simulation lets you test how a facility responds across a full year, rather than relying on a single design-day snapshot. It also allows you to compare design options before committing to equipment and layout.
As rack densities increase, air cooling that works at moderate loads may no longer be sufficient. Engineers need to know when air cooling reaches its limits and where liquid cooling could reduce the burden on the air system. A detailed model provides the evidence for those decisions.
Using a dynamic simulation with sub-hourly annual weather files, lets you evaluate the critical interactions between, and collective performance of: IT load; cooling infrastructure; plant controls; climate impact; electrical demand; and operational behaviour, enabling better informed design decisions.
Use a detailed model to divide the data hall into individual IT racks, cold aisles, hot aisles and related areas. This makes airflow paths and temperature differences visible across the system, supporting more accurate performance modelling and a clearer assessment of temperature differentials.

Figure 2: Detailed ApacheHVAC model in IESVE
Within ApacheHVAC, there is now a new dedicated server rack component, which can be placed within the Airside HVAC network for detailed evaluation of all options. Depending on operating mode and outdoor conditions, return air can be exhausted or recirculated, so free cooling can be evaluated alongside mechanical cooling. You can define rack power density and operating profiles at individual-rack or thermal-zone level, depending on the resolution your model requires.
Early-stage models can represent a row of identical racks as a single thermal zone, with the rack count acting as a multiplier on the IT load. As the design matures, each rack can have its own zone and dedicated settings. Auxiliary and CDU power can be included alongside the main rack load, and consumption can be assigned to a specific electrical sub-meter, allowing energy to be analysed by data hall or facility function from the simulation.
![]()
Figure 3: Air-cooled Server Rack in IESVE
This powerfule server rack functionality simulates IT loads across a full year, with time steps as short as one minute, to fully represent the variations in cooling demand and energy use. Depending on your operational data, you can apply a continuous profile, a standard data-use profile, or a freeform high-resolution profile where every time step is unique. You can workevolve with the information available at each stage, moving from design estimates to measured data.
Airflow controls play an important role in the resulting fan energy and can impact the overall PUE. If airflows operate at a constant volume, the energy associated with CRAH units will remain constant irrespective of the IT equipment loading. Variable speed airflow controls allow the system to adapt to changes in the IT load.
The Server Rack component includes multiple options to model airflow as either constant speed, 2-speed or variable speed which can be controlled based on either the rack entering or rack leaving temperature.
The server rack component will calculate the required airflow needed to meet the design IT equipment load based upon the design entering and leaving conditions to help ensure sufficient airflow is modelled.
Rear-door and top-of-rack coolers remove heat at the point of discharge, so air returned to the hall meets the cold-aisle design temperature. For an active rear-door cooler, you enter the coil’s total capacity, which can be matched to the total rack power. The coil can control leaving air temperature at a fixed value, a specified discharge temperature, or proportionally, and you select the network circuit that meets the load.
An active fan can be added with defined airflow, fan power, control mode, and performance characteristics. Fan airflow can match the overall server airflow, with design fan power updating automatically. The fan properties can then be refined to reflect the selected unit, including its performance curve for variable-speed operation.

Figure 4: Server Rack with Active Rear Door
Liquid cooling can now be modelled through a unique capability offered only by IESVE. As rack power climbs, a growing share of heat can be captured at the chip and transferred away by a coolant loop. IESVE supports direct-to-chip, sidewall and immersion systems.
For example, when setting rack power and what percentage of the IT load is met by direct-to-chip cooling, including delta-T and water loop details, allowing greater use of ambient heat rejection rather than relying solely on air-cooled chillers.
When the liquid-cooling proportion changes, IESVE recalculates heat transfer, fluid flow and the remaining air-side load. The CDU heat exchanger approach temperature is a key input, and the residual air load updates automatically, showing how much cooling still falls to the air system.
![]()
Figure 5: Direct-to-chip liquid cooling
Coolant properties affect heat transfer and pump power. You can select various non-water liquids such as ethylene-glycol or propylene-glycol mixture and set the glycol percentage, with fluid properties assigned automatically. A custom fluid can also be defined using density, specific heat capacity and freezing temperature. The associated pump is modelled as a dedicated component, with power based on transmitted flow and the coolant properties entered for the loop.
Detailed modelling is most valuable when it supports compliance. IESVE provides templates aligned to ASHRAE 90.1 and 90.4 compliance, helping teams build models that reflect these standards from the outset.
IESVE 2026 now lets you represent the racks, loads and cooling systems specific to your systems, and test how design variations perform across the year: You do not need to choose between detail and practicality. Because the functionality is powered by ApacheHVAC, the detailed data hall sits within the environment you already use for building-scale analysis.
To find out more about adding server racks, setting IT loads, configuring airflow, modelling rear-door cooling and setting up direct-to-chip liquid cooling, watch the video at Modelling Liquid & Hybrid Cooling for Data Centres in IESVE 2026 | VE Tech Tips
This video shows how to:
UNLOCK ACCESS NOW
Join a select group of users gaining access to IESVE's premium data centre feature for liquid/hybrid cooling modelling. Purpose-built for the demands of modern data centre design, this premium feature extends your VE2026 workflow with advanced data centre performance modelling and specialised cooling analysis.